And yes ideally I would wait and do more preparation, but for various compelling reasons which I won't go into here, that's not an option
I really hate to be harsh, but sometimes a rude "wake-up call" is what you need, so here it is:
If it is not an option to stop building now, then it is not an option for you to have a successful studio. Period. Stop. End of story. It really is that simple. You CANNOT successfully build a studio without proper planning. It WILL NOT WORK. That's about as categorical and in-your-face as I can make it.
So the choice is yours: Start building tomorrow and fail. Or be sensible, stop building, plan properly, and succeed.
We have seen this happen time and time again on the forum: People absolutely convinced that they MUST build RIGHT NOW, and that their extreme urgency will somehow invalidate the laws of physics, allowing them to bypass the fixed rules of nature that everyone else must live by. Because it is life-or-death for them, the Universe realizes this, and will allow sound to NOT follow the normal rules, but only for their specific situation, just because they are in a hurry.... Sound will bow down to them, because their situation is so important....
Not gonna happen!
Sound waves will behave exactly as they always do, for your studio, just like everyone else's.
In every single case where we have seen this on the forum, not one has succeeded. None. Zero. Zilch. I very much doubt your case will be the first...
In every single case where this route has been followed, where we have warned people to stop, wait, design, then carry on, and they have ignored our advice, believing that they know better, and their situation is "different", not one has ever produced a successful studio. In fact, not one has even produces a studio at all!
Let that sink in for a minute. Why would your case be any different?
The ONLY times that there has been success, is when people have heeded our advice, stopped, planned properly, and built it right. In some cases, they even had to tear down stuff they had built wrongly already, then start again. Such as this one:
http://www.johnlsayers.com/phpBB2/viewt ... =2&t=17363 (read the first few posts, carefully....)
I do hope you won't abandon me, and help me as best you can in these circumstances!
I'll try, but I really don't hold out much hope of being able to help someone who has made a conscious decision to fail.
And my builder already knows the ground as he excavated it to build a patio and a deck. So a monolithic slab is not an option he tells me.
Really? That sounds very strange! The experts normally recommend monolithic slabs precisely FOR difficult ground... I'm wondering if your builder maybe has a vested interest in going with the long, slow, expensive process, that will put a LOT of extra cash in his pocket (a couple of thousand pounds extra, at least, probably...) rather than the fast, efficient, low cost process? I wonder .... Hmmmm..... It makes you think, doesn't it?
Fact: Your builder is NOT qualified to make this decision. A soils engineer or structural engineer is the ONLY guy who can tell you the right way to do this. Period. Do NOT make the mistake of trusting the guy who stands to make a stack of money, when making major, key decisions like this! Trust the qualified, certified export engineer, who has no vested interest at all, and actually does know what he is doing.
Before you do anything, hire one, tomorrow morning. Get him in, and get his report. Tell him you'd like a monolithic slab, and ask if there is any good reason why that would not be good for your situation. Ask him to explain, clearly, what the pros and cons are of the various types of foundation.
There's only one problem here: he'll want to know what total load you are going to put on your foundations, but you don't have a clue about that, because you have not planned a single thing about it! You have no idea at all what your dead load and live load will be: So how in hell can your "builder" tell you what dimensions, materials, and techniques you will need for doing the foundation? How can he even give you a cost estimate, when nobody yet knows how much weight the foundations have to support?
This makes no sense at all....
Does your builder even know how to do a monolithic slab? What specific structural reason does he give you for his suggestion? Not just "Well, gee, umm... I think... errr... I don't like doing it that way", but an actual, structurally valid reason.
Thanks for this summary. From this I read that we're overdoing it.
Why do you think that is overdoing it? Isn't that exactly what I said in my post?
Pine cladding fixed directly onto
OSB board fixed to
Timber framing
Between the batons: Rockwool RW3 100mm insulation (density 60 kg/m3)
Small air gap
Rockwool RW3 100mm insulation
Timber frame
Double thickness fire board (with green glue between) fixed directly to frame
In what way is that different from what I said?
Also, did you use this equation yet? " Fc=c[(m1+m2)/(m1m2d)]^.5 " I gave it to you yesterday, and mentioned that if you do not understand it, or do not know what it means, or have not yet used it, then there is a SERIOUS problem here! It is one of the most basic, simple, KEY equations that you MUST use on your walls, if you hope to avoid failure. "Failure" can take two forms here: 1) you finish the place and the isolation is so lousy that it is not usable as a studio. 2) You finish the place and have much more isolation than you need, which is nice, but it also cost you much more than you should have paid, so the only guy who wins is the builder.... again....
Learn what that equation means. USE IT! Then base your build on the results you get. If not, then there's no point me trying to help you any further.
My builder tells me he's planning a 'warm roof' which I assume is the same as a sealed roof.
"Assuming" is a very, very bad way to design a studio. Starting a build without even having the complete plans in hand, either electronic or on paper, is a plain stupid way of building a studio!
Do you have the complete plans in hand?
Sorry to be so harsh again, but if there's one thing that I'm known for on the forum, is calling it like I see it. No beating about the bush. No pulling punches. No PC crap. Just laying it out in front of you, in all it's ugly glory. IF you start building a studio, and you do not have the plans in place, that's stupid. I have no other way of describing it.
Show me the detailed plans for your "warm roof", exactly as it will be built in your specific case, with all the dimensions, and then I can tell you if it is what you need, or not.
My builder tells me he's planning a 'warm roof' which I assume is the same as a sealed roof. Like the walls, from the outside he's planning weather resistant covering, membrane, OSB board, the Rockwool RW3 insulation, timber frame.. air gap, Rockwool RW3 100mm insulation, timber frame, double thickness fire board (with green glue between) fixed directly to frame
What the dimensions for the lumber? What span? What is the truss design? What live load and dead load did you use for the loading calculations? What deflection are you considering for the joists? What decking will be used? What is the slope of the roof? What is the nailing schedule? What is the membrane? What is the final finish surface of the roof? How much will it weigh? What is the surface density? What is the MSM f0 frequency in combination with the inner-leaf ceiling?
If you cannot answer those questions directly from the plans you have in your hand right now, then it would be foolhardy for you to proceed. Not knowing all of that is sure sign that there is no planning going on here, and that's a certain indicator of failure. Guaranteed.
Let's take this piece by piece:
"weather resistant covering" - What type? How thick? What mass? What surface density? How is it attached?
"membrane" - What type? How thick? What mass? What surface density?
"OSB board" - How thick? What surface density? How is it attached? How are the joints between boards sealed?
"Rockwool RW3 insulation" - How thick? Why? Why not semi-rigid fiberglass? Or fluffy fiberglass? Or cellulose? Or something else? How will it be held in place?
"timber frame" - What dimensions? What span? What load is on that (live and dead)? Wheat deflection?
"air gap" - How big? Why do you want empty air in your cavity, when I already spent a lto of time explaining that your cavity should be completely filled for maximum isolation? Did you not understand the difference between the constant being 43 or 60 in the equation?
"Rockwool RW3 100mm insulation" - Why?
"timber frame" - Dimensions? Span? Load? Deflection?
"double thickness fire board" - What thickness "fire board"? What is "fire board"? Surface density? Attachment? Seals?
"with green glue between"- Why? What coverage pattern?
Etc.
So many questions... and I'm betting there are very few answers...
(not using resilient clips as I believe it's decoupled inner room)
You just "believe" that it is decoupled? You don't KNOW this for a fact? Yet you plan to start building tomorrow?
Above the inner leaf will be acoustic venting ducts that lead down to vents in the inner ceiling for air in and out (if need be with silencer boxes mounted under the inner ceiling).
Where is the AHU? What is the heating/cooling/dehumidifying capacity of that unit? What sensible heat load did you consider in your calculations when you decided on that unit? What latent heat load? What occupancy? What flow rate did you calculate you need for your room? What will the flow velocity be at the registers? How much make-up air will you be adding? How much stale air will you be dumping? What size duct work is the correct size for this situation? Will that be rigid or flexible? Lined or not lined? What will the static pressure drop of your system be? Can the AHU handle that static pressure load? How will you prevent the pipe bundle from flanking between leaves? Where will the heat pump go? Where will the condensate drain go?
If you did not understand all of those questions immediately, without googling them, and if you don't have all the answers in your plans already, then you have no business building this place yet: it will fail, since it will not be ventilated correctly.
The simple, and rather silly, explanation that your builder gave you of " venting ducts that lead down to vents in the inner ceiling for air in and out" shows that he does not actually have a clue about studio HVAC. What on earth is an "acoustic venting duct"? I've never heard of one of those! I've been designing HVAC systems for studios for many, nany years, and I have never come across that term ever before. Because it's somthing your builder invented himself, on the spur of the moment, since he doesn't actually have a clue.
(if need be with silencer boxes mounted under the inner ceiling)
You are kidding, right? Do you have ANY idea how BIG such boxes are? Clearly not. I certainly would not want one of those hanging from the ceiling in my studio!
Take a close look at this image: it shows the dimensions for the HVAC duct system for a small control room that I designed for a customer a few years back. The room is very similar in size to your room, so you WILL need something like this:
Typical-studio-HVAC-duct-and-silencer-system-with-dimensions.jpg
That is a "bird's eye view" from above the control room ceiling, looking down onto the inner-leaf ceiling, with the outer-leaf removed: all of that HVAC system goes in the space between the inner-leaf ceiling and the roof (or middle-leaf ceiling, as the case may be). Do you REALLY want all of that hanging from your ceiling, inside the room?
(This is probably the point where you and your builder will come up with a whole slew of reasons why you think you don't need an HVAC system for your room, but I can tell you in advance, before you even mention them, that I've heard them all before, and not one of them is valid: you DO need an HVAC system for your studio, if you plan on staying alive and healthy in there. There is no argument here. HVAC is not a luxury for a studio: it is a basic requirement. It is every bit as necessary as having a roof on top and walls around you. So please don't even wast your time trying to tell me why YOUR case is different, and the universe will also suspend the biological laws that govern your metabolism and how your respiratory tract works, just because you are in a hurry....

)
But also, will a sealed roof like this be OK?
I have no idea, until you show me the detailed plans. I have no idea what your builder means be "sealed roof" or "warm roof". Different meanings to different people in different building codes... A quick check on Google found this "definition": "A warm roof construction has many benefits over a traditional ‘cold roof’, essentially it is a ‘breathable roof construction’, which allows moisture to escape which in turn prevents damp and any associated decay problems. " If it is breathable, and allows moisture to escape, then it is NOT sealed, so it is NO use for your situation, unless you also add in a middle-leaf.
Or do I need to do the middle leaf to address a possible condensation issue?
Based on the above definition, it certainly seems that way! On the other hand, since your builder doesn't seem to know what he's talking about with foundations or HVAC, it is enturely possible that he's misusing the term "warm roof" as well, and to him it means something totally different. I can't tell what he has in mind until you show me the actual final plans for your specific "warm roof". Show me those, and I might be able to say. But I'm not talking about generic plans for other warm roofs: I'm talking about the specific, actual, real plans for your specific studio, drawn in complete detail, and approved by your local authorities. Show me those plans, and I can tell you if that will work, or not, acoustically.
I believe I have checked all the regulations.
Are you certain? The most recent version I have is 978-1-4098-5046-5, dated April last year. IS that what you have? That's what I used the last time I designed a studio for a customer in the UK. I'm assuming you are presenting this as a Class E situation?
You say the ground slopes slightly? Did you notice what point you have to measure your 2.5m, 3m, or 4m height from? Did you notice that, regardless of the height of the roof peak, your eaves cannot be higher than 2.5m? No, I didn't think you noticed that. Did you realize the implications of this limitation? No, I figured you didn't realize that either: it places a limit of 2.5 m on your outer-leaf wall height (since that is where you MUST measure your eave height), which implies an even lower height for your final inner leaf ceiling. Depending on span and construction, and allowing 40cm for the silencers, your final inner-leaf ceiling will be around 2m, maybe lower. Explain to me how you hope to get usable control-room acoustics for a ceiling that low... That's a little under 6'6".... (I hope you are not too tall, and don't get claustrophobic...)
You mean you did not know this already? That your assumptions and lack of understanding would lead to a room with an unworkable low ceiling height? You would have soon figured that out, if you would have planned properly.
Here it is, in black and white. Page 44:
Permitted-development-eaves-extract.jpg
So no matter how high your roof can go, your walls CANNOT exceed 2.5m at the eaves. And that places a severely low limit in the inner-leaf ceiling.
I can go up to 3m
... assuming you do a shed roof, that's possible, yes. And for a gable roof, it could be 4m! But as paragraph (f) clearly states, your walls can be no higher than 2.5m at the eaves. THAT is the problem, not what you ASSUMED was the problem.
see attached snip from the local government website.
I'm well aware of what permitted development regulations for the UK state: I have designed several studios for customers, under these. One of them is Kirby's place, that I linked you too. And the above is the exact reason he decided to bight the bullet, and dig deep. His "eave height" is exactly 2.5m, but the internal outer-leaf shell height is 3.5m (11'5", roughly), and the inner-leaf ceiling height of his control room and iso booth, (with complete HVAC above) is 2.8 m (about 9'2"). Very decent, and very usable, acoustically. The final visual ceiling height in the control room, with all acoustic treatment in place, is 2.66m (not counting the cloud, of course). That's about 8'6" in imperial.. Higher even than the standard UK ceiling height, of 2.4m...
But I believe what I am doing will give me the isolation I need.
And fifteen years ago my kids believed in Santa Clause... but then they grew up, learned about reality, and now they no longer believe in that....

In other words, what you BELIEVE and what is REAL can be two very different things. The only way to tell if you will have the isolation you need, is to do the math. Just believing it to be enough will not make it so, any more than a small child believing in Santa actually makes him exist.
Believing and hoping and assuming, and guessing are really, really terrible ways to design a studio...
Finally, I did look at the threads you suggested. Some very impressive work indeed.
Take a close look at Kirk's thread: That is exactly what you need, and was built under Permitted Development, Class E. It's not far-fetched, "out there", or unreasonable: it is realistic. His will have a bathroom, kitchenette, isolation booth, control room, and entrance lobby. All within a 33.5m2 footprint. You could do the same. Or you could go smaller, and skip the extra rooms, leaving just the control room. Which is nearly 15m2 floor area, in Kirk's case, and could be about the same in your case.
I am honestly not aspiring to that level at this point in my life.
Then I don't understand what you are aspiring for! If you are NOT looking for a workable, usable, realistic control room on a 25m2 footprint with good isolation and good acoustics, built under Class E permitted development rules, then I must have entirely misunderstood your thread! That's what Kirk's thread is about.
Stuart, I know it's not what you like hearing, and I totally realise you have my best interests firmly in mind, but this is happening and I'd rather put out to sea in this craft with you as a virtual mate.
I'm not going out to sea on a boat that I suspect will sink! I'll happily watch from shore, and shout encouragement every now and then, if you want, but I do hope you know how to swim, because your boat ain't gonna float...
- Stuart -
PS:
DIG DOWN BELOW GRADE!!!!
YES!
Your silencer boxes and HVAC take up a TON of room.
YES!
Your ceiling height will be very very short if you don't go down some.
YES!
You NEED the height!
YES!
Also, I understand there is some "compelling reasons" you have to start the build now. I won't say that's fine
Neither will I! In fact, I'd say that unless the "compelling reasons" is a guy standing next to you with a gun against your head, telling you he will pull the trigger unless you start tomorrow... then there's no reason at all to actually start tomorrow. It's foolish.
This is like he said he wants to go on vacation, and is leaving tomorrow: You ask here he is going, and he says "No idea". How are you getting there? "No idea". Plane? Train? Car? Bus? Bicycle? Roller-skates? "No idea". How long will it take? "No idea". What clothes did you pack? "No idea". How much will it cost? "No idea." What will you eat? "No idea". Do you have any idea at all where you are going? "On vacation! And I really REALLY have to leave tomorrow... even though I don't have a clue about where I'm going or what I'm doing"....
That's what I'm reading above.
You literally cannot build something this complex without a 3D plan and a bunch of calculations.
YES! Very, very true.
I hope *fingers crossed* that I see a deep hole being dug. . .
I'd differ slightly here: I would MUCH rather see nothing at all happen tomorrow, except that the entire thing gets put on hold, and common sense takes over....
But I'm not expecting to see that either....