Hi Greg & Stuart!
I've had a chance to review all this great information and I'm very happy overall because I wasn't totally off track....just confused with certain numbers.
I have slightly different lower numbers because of the ceilings. I was told since the room is basically a triangle that I should take the total height and divide by two, so in my case ceiling height is 7'.
Control Room
Width: 19' Length: 10' Height: 7'
SQ/FT: 190 sq/ft
Air Volume: 1330 ft2
Required Air Changes per/hr: 6
Total Air Volume to move each hour: 1330 x 6 = 7980 ft2
Required CFM: 7980 / 60 = 133 CFM
Recommended Branch Duct Size: 8" Round-Duct
Required Fresh Air @ 30%: 133 * 0.3 = 40 CFM
Silencer Internal CSA @ recommended 200 FPM: (133 CFM / 200 FPM) * 144 = 96 in2
Silencer Inlet CSA: 96 in2 / 2 = 48 in2
LiveRoom
Width: 19' Length: 13' Height: 7'
SQ/FT: 247 sq/ft
Air Volume: 1729 ft2
Required Air Changes per/hr: 6
Total Air Volume to move each hour: 1729 x 6 = 10374 ft2
Required CFM: 10374 / 60 = 173 CFM
Required Fresh Air @ 30%: 173 * 0.3 = 52 CFM
Silencer Internal CSA @ recommended 200 FPM: (173 CFM / 200 FPM) * 144 = 125 in2
Silencer Inlet CSA: 125 in2 / 2 = 63 in2
With all this above and based on your help:
Total cubic feet of the studio: 3059 ft2
Required airflow rate for my main trunks would be: (6 air changes per hour X 3059 cubic feet )/60 min = 306 CFM
If I was to keep my current main trunk as is as a rectangular 8"x10" duct I would have a velocity of: 306 / (80in2 /144) = 546 FPM with a Friction Loss of 0.061 wc/100ft
If I was to change my current main trunk from 8" x 10" to a 10" round duct I would have a velocity of: 306 / (78.54in2 / 144) = 561FPM with a Friction Loss of 0.054 wc/100ft
If I was to change my current main trunk from 8" x 10" to a 10" x 10" rectangular duct I would have a velocity of: 306 / (100in2 / 144) = 440 with a Friction Loss of 0.035 wc/100ft
Yes, but 80in2 of round duct is NOT the same as 80in2 of rectangular duct! Round duct has lower surface area, and therefore lower friction loss. You need to check the actual conversion factor, based on the rectangular dimensions:
Using the simple formula (CFM = FPM / CSA), seems like the velocity would be lower using my current 8" x 10" rectangular duct (546 FPM versus 561 FPM) but understand that the friction loss would be greater than using a round duct (0.061 versus 0.054).
Question: Would the friction loss difference have that much of an impact on my total system?
Again, the current trunk system that's already been installed is a reducing plenum type that starts from 16" x 16" down to 12" x 10" down to 10" x 10" down to 8" x 10"
I guess my options are: A) Keep the current configuration or B) Transition from my current 10" x 10" to a 10" round duct. Note that I have no problem going with option B, I just want to make sure I wouldn't be going through all this trouble and extra cost for something that in the end wouldn't make that much difference.
You seem to be missing the point: The purpose of duct liner in a studio is NOT for thermal reasons, but for acoustic reasons (OK it is for thermal reasons as well, but mainly acoustic). If you put insulation on the outside, that is only thermal: it helps reduce heat loss through the walls of the duct, but doesn't do much for the acoustic issues INSIDE the duct...
You can probably skip the internal duct liner for any ducts that you run in the cavity between the leaves, but not for ducts that are outside the outer leaf, or inside the inner leaf.
Yep, I kinda figured it wasn't for thermal reasons when used for studio applications. Since the entire duct system will be in between the inner and outer leaf..I will be skipping the duct liner in the main trunk, but will put liner in all the silencer boxes and sleeves.
Check the manual for the AHU: Most have at least three different fan speed settings, and each one produces a different CFM / fpm combination. Some have more than 3 settings. As long as one of those settings is close to what you need for your room, that's fine. If not, then you have two choices: 1) sell that unit and buy one the right size, 2) dump the excess air flow to some other place: either throe it away back to the outside world (very inefficient!) or use it in another part of the building. Since Dumbledor is dead, he can't help you here!
Here are those details from my AHU. Note that my unit is the 08 model.
MX-AHU-DETAILS.png
If I set the fan speed on low looks like 558 CFM with an external static pressure of 0.5 would be the lowest it could go. I suppose this would mean I would need to design the system and aim for 0.5? Do you guys think 558 CFM would be too much? If that's the case, I will add branches to dump the excess air into the room next to the HVAC closet. It's an unoccupied section of the house that will be used as a storage area.
Question on how to use the ASHRAE DFDB app....for Equivalent length of all the fittings. When asked to input a CFM value for the fittings calculation...should I be using the 558 CFM that my AHU will be pushing or the 306 CFM that's required? That part confuses me still.
Another question about the fresh air and HRV requirements of the studio. As calculated by Greg if my fresh air requirement is 30% and is represented by 306 CFM * 0.3 = 92 CFM. Does this mean the branch ducts going to the HRV unit has to be sized on 92 CFM and most importantly do I add that to my total CFM requirements of the AHU? Just curious to know if that is totally separate from AHU.
... and therein lies the problem! HAVC should never be oversized or undersized too much, for several reasons. As you have already discovered!

HVAC should be sized correctly for the job.
Right and I can see how this can be a big problem if not sized properly. I think I'll be okay based on all the information I've got so far. My best option if it becomes an issue is to dump the excess into the adjacent room next to the HVAC closet.
I'd suggest splitting the airflow inside the silencer, to a pair of outlets that total around 120 in2, so 60 in2 each, which is roughly the equivalent of an 8.4" round duct, x 3 = 25 inches. So your "through-wall sleeve" should be about 24" long, total, from the furthest point inside the silencer box, up to the register. That's not too bad: assuming the interior depth of the silencer box is 10" (because you plan on using 10" duct, so it has to be at least deep enough for the duct to attach!), and that you have 2x10 joists, plus a 1/2" gap between silencer and joist, that already gives you 20" of depth, so the sleeve would only need to extend another 5" or so below the joists.
That's all theoretically optimal: if you have a lower flow rate, you can go with a shorter sleeve. If you hide the register inside some type of acoustic treatment as I often do, then you can use a shorter register because the treatment itself diffuses the air flow, and helps to quieten any noise.
Excellent! I will plan to do exactly that and split the airflow inside the silencers. I plan to secure the silencers on the support beam as seen in the pictures of my previous post. That will give me enough room to have a long enough sleeve to meet this requirement.
As for the decoupling of the silencer boxes from the inner leaf ceilings of each room, as stated above I plan to secure the silencers on the support beam above each room with straps and probably some sort of rubber strips. They will not be touching the inner leaf ceiling of the rooms so I suppose I could consider this decoupled as the only material that will touch the sleeve of the silencer and the inner leaf ceiling (drywall mass) will be the best caulking I can find.
Thanks again for everything guys!

this starting to make more and more sense to me and will be able to progress with my HVAC installation.
Francis,